we arent allowed to lift boards or move any heavy furniture for eicr's as per request of the landlords/letting agents

certainly wouldnt be ticking the box off if i hadnt found any though! lol
 
Did you disconnect ALL the CPC's from the CU and do a Ze?

That said how many circuits are there?
 
Did you disconnect ALL the CPC's from the CU and do a Ze?

That said how many circuits are there?
Yes..and got no reading as there is no main earth connected. I could only get a Ze reading between the CPCs and incoming L and N.

3 circuits connected

Lights sockets and oven
 
I had similar. an EICR stating TNCS when there was no earth (6,000 Ohms or so). The quoted Ze must have been taken either on a l&n two wire test or a l & both connected to n 3 wire test as it was the correct figure! Just to be absolutely certain that the earth conductor hadn't somehow been removed my son got permission to dismantle the cutout and was able to conirm that there never had been a pme connection.
The author of the periodic was not a scheme member so no joy there and trading standards couldn't have been less interested, however he did not want me to remove the earth from his own house.
 
I had similar. an EICR stating TNCS when there was no earth (6,000 Ohms or so). The quoted Ze must have been taken either on a l&n two wire test or a l & both connected to n 3 wire test as it was the correct figure! Just to be absolutely certain that the earth conductor hadn't somehow been removed my son got permission to dismantle the cutout and was able to conirm that there never had been a pme connection.
The author of the periodic was not a scheme member so no joy there and trading standards couldn't have been less interested, however he did not want me to remove the earth from his own house.

The more complaints they get, the more interested they do get ....
 
The R1+R2 doesn’t necessarily need completing on a eicr as that is a requirement of initial verification confirming earth continuity before new work is put into service.
Doesn’t preclude its use of course If you want to carry out the test, but one of the ways to confirm earth continuity is a zs test.
You must remember that the installation is already in service.
I like to go round with a wander lead from the MET to test all exposed conductive parts as part of the eicr before completing a zs test.
 
Can you clarify why she was told that the walls would have to be chased to rectify the problem?
I assume she had agreed to have the option of a lighting rewire ?

How are the tails from the cut out on the downstairs routed,are they buried or enclosed in conduit pipe and where is the meter?
 
Can you clarify why she was told that the walls would have to be chased to rectify the problem?
I assume she had agreed to have the option of a lighting rewire ?

How are the tails from the cut out on the downstairs routed,are they buried or enclosed in conduit pipe and where is the meter?
Can you clarify why she was told that the walls would have to be chased to rectify the problem?
I assume she had agreed to have the option of a lighting rewire ?

How are the tails from the cut out on the downstairs routed,are they buried or enclosed in conduit pipe and where is the meter?

I told her walls had to be chased as I couldn't do a CU change without CPCs in place on the lighting circuit.

Tails are fed from downstairs cut out in armoured cable, run surface through a cupboard, through some boxing in, then into a small electrical cupboard to another cut out with the meter.
 
dave,have you read the guidance given in the link I have provided?,its why I used the word option in my post
https://www.----------------------------/mediafile/100126675/Best-Practice-Guide-1.pdf

What size is the armored cable and how is it terminated?
 