The thing is with those type of hobs is that the combined load of all 4 hobs is about 10kW..
When all hobs are switched on the overall load is reduced..
In some instances I would apply diversity; such as the overall maximum demand but not for a single supply to this type of hob if it is known that it will be used at full power for long durations
Fair point. Although I've never had any issues with similar rating induction hobs on 32 amp circuits before.
 
The main problem I’ve had with them, is the increased earth leakage on the installation, tipping the RCD over the threshold
 
The main problem I’ve had with them,

The main problem I've had with ours, is the friggin mess they make and the amount of cleaner etc to remove the muck from the glass.

Much prefer our old gas hob. :)

PS, our one is a four zone one. We'd struggle to put four saucepans on it; couldn't see anybody else doing so with theirs.

Inbuilt diversity.
 