The rating you are quoting (15kw) and the diversity permitted, would be the maximum that the 32 amp circuit would be designed for
If this was feeding another piece of equipment, then the maximum demand of that circuit may exceed the rating of the cpd
For cookers or hobs above 2kw I would use a dedicated circuit
Below this level it would depend on load factors of the kitchen and/or household appliances and the circuits existing
If it was a new installion then I would use a dedicated circuit whatever size the cooker/hob