i usually go for 100% inspection of accessories on domestic, unless i really need to save time (i.e. The customer is that tight fisted). Used to do 50% sampling, until one time i missed a diy lashed up cooker switch that later almost melted, and i had given the installing a 'satisfactory'. I know you can't check everything, as most of the installation is hidden away, but i like to check everything i can get to nowadays. Right down to checking fuse ratings in fcus.

incidentally, this brings me onto another issue i encountered recently. As far as i am concerned, stuff on a plugtop isn't part of the fixed wiring, but what would you guys do if you came across a terrible arrangement of six socket outlets (screwed to the wall) fed from flex going all around the room and plugged into a single socket? Room only had the one socket and there was a heater, tv, pc and other stuff plugged in.
.....3
 
I will tell how they do
Ze test done
Turn cu off, link L to E on whole board
Run around taking R1R2 at furthest looking outlet on each circuit
quick calc for Zs
rcd test at board if there is one
no IR test no cont. test
jobs a goodun

That must be a landlord PIR then ....
 
I think its great i had a supervisor who could rewire a 3 bed semi in 1 day must be the same sparks
 