HiI have just test a couple of phone chargers in my house using a Kewtech KT71.When i have pressed the class 2 test it goes through it sequence and then fails on insulation, but if i press the test again (still on the same test i think)it passes. Now if i was doing this test for real would i fail it because initially it failed, or should i pass it because i pressed the test again and it passed?Hope you understand that.Many thanks
 
Could it be the electronics inside the charger having an efect that looks like the insulation is leaking?
I have the same problem with filtering capacitors on 3 phase inverters which look like an earth leakage fault untill the capacitors are charged.
A right pain I must say because they are powered from an RCD and it keeps tripping.
Do your phone chargers (double insulated and all that) have a plastic earth pin or is it metal?
 
I've seen cheap chargers and 5 into 1 multiplug adapters that have a neon power indicator that has one leg on the earth, these are invariably borderline with an IR test.
 
Could it be the electronics inside the charger having an efect that looks like the insulation is leaking?I have the same problem with filtering capacitors on 3 phase inverters which look like an earth leakage fault untill the capacitors are charged.A right pain I must say because they are powered from an RCD and it keeps tripping.Do your phone chargers (double insulated and all that) have a plastic earth pin or is it metal?
To tell you the truth i am not sure now because i threw them away because i have spare ones so not sure what they were.Would that make any difference though
 