Sounds like old wiring in a property that has been subject to DIYing. On the face of it the Live and Neutral seem OK but do an R1/R2 to confirm as Glen says that you have a continous earth path. If you do have an earth path Id be tempted to open up each socket and look at the wiring configuration ---time consuming I know. You've got a parallel earth path in there somewhere reducing the value. If there arent any obvious additional wires then it may be as Sparty says, you have a path somewhere junctioned off the CPC thats lowering the resistance. Be interesting to know if you eventually track down the root cause to the CPC or something on the live/neutral!!
And Biff your right ....... a lot of continuity testing & checking eating up valuable time!!