but as r1 and rn are about the same this points to the readings being ok and i ring on a 3 bed semi also looks about right no loose connections etc in sockets or at board. not finished job as we will be back in the morning when i will do all the tests at each socket
does it?..
 
does it?..
yes i think it does to get a high reading on both which from loose bad connections that read about the same would be some bad luck don't you think

im open to suggestions though whats your thinking being them being high not the cpc being lower
 
it may be that a section of the `ring` is without a CPC...and the CPC from the sections that have it have been jointed someware...to create the illusion of a CPC throughout the whole of the ring...so...
an R1 R2 at every point served should verefy this.....
 
it may be that a section of the `ring` is without a CPC...and the CPC from the sections that have it have been jointed someware...to create the illusion of a CPC throughout the whole of the ring...so...
an R1 R2 at every point served should verefy this.....

no its all twin t+e (what i can see ) ill be doing the r1r2 at all points tomorrow i was just starting this when the lad showed me the 1mm so i got rid of that first .
if im right on the lower cpc do i need to put this on cert ?
 
no its all twin t+e (what i can see ) ill be doing the r1r2 at all points tomorrow i was just starting this when the lad showed me the 1mm so i got rid of that first .
if im right on the lower cpc do i need to put this on cert ?
what you doin here?...an EICR?...if so then just make sure it meets disconnection times....
you`v got 2 choices
you get an R1 R2 (recommended here) on every point of the ring....or you go with the end to end resistances obtained and get your points on a Zs...all of em...that would be the easier way....
summats not rite though....
if it meets disconnection times then go with it....
how old`s the install (estimated)?...
any signs of alterations/additions?
RCD`d?
just be on the lookout for stuff won`t you...as if this is giving back the values you have described then there may be other `nastys/anomalies` lurkin....
 
Both the R1 and Rn readings equate to just under 50m in length and the R1+ R2 is appropriate to these readings. It's the R2 reading that is lower than expected, but this is very common on existing installations. Unless I'm missing something
 
Here's an idea- discon. all the other cpc's and check r2 again?

Its almost as if there's a section of the ring with a 10mm bond to a pipe & another bond to the same pipe from another point in the ring
 
its threads like these that remind me why i favour radials these days.
lifes too short to waste it on endless continuity tests lol.
;-)
 
Sounds like old wiring in a property that has been subject to DIYing. On the face of it the Live and Neutral seem OK but do an R1/R2 to confirm as Glen says that you have a continous earth path. If you do have an earth path Id be tempted to open up each socket and look at the wiring configuration ---time consuming I know. You've got a parallel earth path in there somewhere reducing the value. If there arent any obvious additional wires then it may be as Sparty says, you have a path somewhere junctioned off the CPC thats lowering the resistance. Be interesting to know if you eventually track down the root cause to the CPC or something on the live/neutral!!

And Biff your right ....... a lot of continuity testing & checking eating up valuable time!!
 