Feel like I’m posting on here every week for advice :) is a reading of 0.18 megaohms between neutral and earth enough to trip and RCD. Sent to an intermittent Rcd tripping, everything else seems clear bar this one cable. As always nothing tripping while I was there. Ramp tested the RCD and 15ma was the result. Seems very low to me
 
is a reading of 0.18 megaohms between neutral and earth enough to trip and RCD

No, would need to be around 500 times lower to be a real problem. Use ohms law. Say there's 5V drop in the neutral conductor total, i.e. 5V across the N-E insulation. To get 15mA leakage would take 5/0.015 = 330 ohms or lower.

But as I was posting elsewhere yesterday, an abnormal low IR that doesn't itself cause a trip can nonetheless act as a beacon to show where a cable is damaged that might cause intermittent tripping for some other reason.
 
15ma ramp test is about the lowest it can be for the RCD to be considered within spec. Was that with all loads on or with loads isolated?
Finding intermittent trips on an Rcd board can be a right pain. Anything with a thermostat or a timer is a suspect, eg fridge/freezer self defrost, immersion heater.
Kettle, cooker ring/oven element.
Occasionally a smart meter.
Best of luck!
 
15ma ramp test is about the lowest it can be for the RCD to be considered within spec. Was that with all loads on or with loads isolated?
Finding intermittent trips on an Rcd board can be a right pain. Anything with a thermostat or a timer is a suspect, eg fridge/freezer self defrost, immersion heater.
Kettle, cooker ring/oven element.
Occasionally a smart meter.
Best of luck!
Loads were connected at the time, yeah its a needle in a hay stack at times
 
If loads were connected you shouldn't really be testing L and N separately to E, only in parallel. Otherwise the test voltage appears across the load and can cause damage in theory (although usually OK). 0.18 meg is typical of surge-protected leads and adaptors. Did you try a test at 250V?
 

Reply to Intermittent Tripping Rcd fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
307
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
759
Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock