buy a megger does exactly what it says on the tin. not bells and whistles on some

Thanks Wilko, I've been running around disconnecting odd items, any switches with neons etc, tv boosters, anything & everything but not sure what else it could be. I'll try the cont test across N-E Monday cheersA couple of late night thoughts
Looking at manual, it seems to say current is limited to 2mA during IR measurement. This perhaps means that by 15V the circuit is passing 2mA and the mft stops the measurement. This would imply about 7.5k Ohms resistance N-E. You could try to measure the resistance directly using mft continuity function to confirm, for what it's worth.
Perhaps there is still an appliance connected, a polarity issue?
Wow that's so cool of you mate, have you seen IR issues with your 1721 then ?@Soulsurfer, My wife is coming over to Jersey on Sunday visiting family for a week. I have a Martindale IR tester (nearly said Megger). I am happy to lend it to you for the week if you think it would help. She said she is happy to take it for you. PM me if you would like it and we can swap details.
I have a Megger 1721 and sometimes use the old IR tester if peculiar things happen, MFT's do speed up the job but they can waste a lot of time also.
You're an absolute star Paul, cheers and when you're next over ( if you are ) let's get you out for a beer & thank you ! Thanks again, I'll pm in a few mins mate, MattNothing really a problem sometimes I pick up a stray voltage and it stops ramping up, it is a lot quicker to shove the old IR tester on, at least you know what you are getting.
Wife is arriving Jersey this Sunday 6th and flies back Sunday 13th so it sounds just right. I'll probably take out the 6 AA cells to save weight in the hold luggage. If you are happy with this PM me with contact details and we can set it up. I am just sorry I am not going this time, I would enjoy giving you a hand with the fault.
Best of luck next week.
Paul
Hey Richard, I don't think there was any error symbols or anything bad on meter at all, just wouldn't fire up anything to do with N & E.Perhaps see what resistance result you get with an autoranging multimeter to give you an idea of what may be happening, but do check that there is no voltage present first.
The manual does say capacitative loads would cause the voltage to rise slower than expected but I cannot see that there would be a capacitor (or enough capacitance in a circuit) across N-E.
Does the MFT not show any error graphic on failed testing?
Just works perfectly straight to full test V at around 550V dc on the 500 range and >999Meg on screen.^^ what happens when you test a bit of random cable?
Not found any yet but anything is a possibility in this place, found a random old square junction box from old wiring stashed under floor upstairs too and is all over the place cables old and new in a spaghetti mess ! Thanks.^^ in which case the installation must have a fault ...............
Got any downstream RCD's - they can give off very odd results?