this one got me stumped today, new cu fitted all circuits tested out ok apart from IR readings L/E on cooker circuit giving a 12Meg reading (every other circuit >200)

disconnect earth from bar and fault clears and recheck other circuits also all clear, reconnect cooker earth and 12M reading returns, i know its above limits but cant find any reason why its lower.

any ideas?
 
Have you looked where there are connections, there may be a nick in the insulation somewhere. Disconnect cooker from conn unit to indicate whether its the cooker or circuit. Disconnect switch as that could be mildly faulty?
 
electronics in cooker control/clock/etc.
 
Damp in the wall?

Or previously had a bit of a leak/flood there
 
Last edited by a moderator:
Actually brain not in gear, if N/E still up at plus 200 then unlikely just down to damp, unless damage to sheath on that side and damp (he says clutching at straws lol)
 
youve not got any neons in the cooker control switch combined with a TNCS earthing system ,can get some funny old readings with them ,switch not wired in and out reversed
 
actually emoved the switch but it comes back as soon as earth back into earth bar ant figure it although come to think of it there didnt appear to be a cooker outlet plate wonder if thats been buried (gas cooker)
 
If you disconnect the E from the earth bar and you test L/E on the cable and all is fine then is the fault between L of the cable and E of the rest of the install? (straw clutching)
 