Discuss Is this true? BS1363 current rating. in the UK Electrical Forum area at ElectriciansForums.net
I believe most, if they comply to the standard 2G sockets are rated at 20A total. And the issue depicted would occur because that one socket is overloaded or is suffering the effect of a bad connection, either the pin/contact interface, the fuse/terminal/pin interface.
[automerge]1594579863[/automerge]
Should have included... with each socket being rated at 13A maximum.
To comment on the statement they made... I tend to use 2 single socket outlets if there are going to be two hungry appliances supplied by them.
BS1363:1995 requires a double-socket to handle 20A total load; the test conditions are 14A on one and 6A on the other. From P=I²R we note that the total heat dissipated under these test conditions (with the abnormal 14A load) is greater than with 10A load per socket. Therefore, continuous satisfactory operation would be expected with two 2kW heaters plugged in. In a 120V equivalent power context, that is like being able to take 38A total from any ordinary duplex receptacle, an unusual requirement I think you would agree.
Note that the total load limit of the two sockets is a different parameter to the maximum circuit cable through-current. There is an important difference between UK and US sockets here, in that UK sockets only ever have one terminal for line and neutral, so the incoming and outgoing cables are always in intimate contact when correctly installed. There is no snap-out link or side wire/back wire/back stab interconnection to take into account. A normal BS1363 socket will take 32A passing through the terminal, as necessary on a 4mm² 32A radial.
The damage shown in your picture is specifically caused by a defective fuse clip in a moulded plug where the fuse lies crossways above the L & N pins. That was not caused by any defect in the socket or general overload.
Not unusual if you wanted to run two heavy devices (like resturant equipment) from a single duplex which is typical in diners and cafes. My understanding is that you could pull 40 amps (20+20) through a NEMA receptacle if you broke the tabs and ran two circuits. In a single circuit application you are limited to a 20 amp breaker. In the two circuit application each half of the receptacle is still rated 20 amps.
In order to make the 40A / 4.8kW available at one duplex, as you say it would be necessary to run two circuits or one multi-wire circuit for just that one outlet, which would not be done generally throughout an installation. High loads would then be concentrated at the outlet known to be equipped for them, making its heavy usage a self-fulfilling prophecy. In contrast, every double socket in a normal home wired with BS1363 sockets on 32A circuits is capable of supplying 4.6kW, therefore there is no inclination to concentrate load at a single 'special' socket. Whilst there is nothing to prevent 26A total being used, the effects of such usage persisting long enough to cause damage would be buried in the noise of random differences between different brands of socket, plug and operating environment. I have studied many damaged sockets and have never seen any where excessive combined current was definitely responsible for damage, absent other problems like improper cable termination.
Right, the rest of the installation would place the duplex receptacle on a 15 or 20 amp breaker which would trip if the duplex was subjected to more than 15 or 20amps well before it overheated.
Right- you know said receptacle being used for two 16-20 amp loads each with a NEMA 5-20r cord cap. What stops me from taking a single duplex, breaking both hot tabs, then running two circuits and a shared neutral? 32 amps continuous or 40 amps intermittently? The receptacle would not over heat.
Both scenarios are covered- but not with a BS1363 socket.
In dealing with out-of-specification occurrences that are not protected against, it's important to consider the severity of the consequences. Typically, a double 13A socket subjected to 26A total load for a typical duty cycle will not 'overheat' in the sense of melting or catching fire. Its service life might be shortened, or the plastic might discolour sooner, or some such progressive deterioration caused by the additional temperature rise. Manufacturers can and do make accessories that exceed the BS specification, either explicitly in their ratings or through proven reliability despite the rating being exceeded.
From personal / anecdotal experience I would rank the root causes of thermal damage to BS1363 socket outlets in the following order, most common first:
Faulty fuse contact in plug (heat conducts through line pin and damages socket contact and faceplate)
Loose terminations in plug.
High-resistance contact between plug pin and socket contact, through user-inflicted damage, thermal fatigue, corrosion or poor design.
Loose terminations in socket.
Usage for high, continuous load (per 13A socket, ignoring total) without occasional mating cycles to remove oxide buildup at contact interface.
All other factors (including switch resistance, excess total load, high ambient temp)
Can you explain what breaking the hot tabs means? Is this some way of seperating a twin USA type socket so that you can wire to each of the individual outlets separately?
BS1363 sockets only have one set of terminals and you cannot feed each side seperately.
Yes, most NEMA duplex receptacles have two sets of terminals linked by the flat pieces of metal that you can see projecting at the side between the screws. These can be broken off to separate the two halves. Traditional side-wiring using the binding-screws only accommodates one wire per screw, so the circuit through-current would pass through the tab. Some products have a rising clamp back-wire terminal incorporated, that will allow for two cables per terminal with the tabs out.
Yes, each half of the receptacle can be separated electrically and fed by its own circuit. There is a metal "bridge" that can be removed on each side of the screw terminals.
Page from Bs1363-2016
Reply to Is this true? BS1363 current rating. in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Hi All I'm a professional mobile app developer. Around 12-13 years ago I created a couple of apps for the fire protection / safety industry that...
We might need to have a small 3-phase DB in an industrial location that might be exposed to the elements occasionally, though normally it will be...
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...