If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
This is an elaboration of a previous question.

It is my intention to have a smart meter installed and an isolation switch at the same time. Just waiting on a date.

However, given three days of storm power cuts I am now also thinking of adding a transfer switch so that my 8Kw petrol generator (16amp and 13amp outputs) can be plugged in to the main house CU (limited circuits, no EV and kitchen is on a separable circuit with its own RCBO and CU). Supply is 100amp single phase, T-N-CS.

I am wondering if a transfer switch would in effect do the same job as an isolator? At first sight at least it seems logical as the purpose of the transfer switch is to prevent generator power going back down a supply line. Obviously if used as an isolator, then the generator would not be plugged in.

Generator is an outside Honda unit, pull start rather than auto. Clearly put in a suitably ventilated place.

The main house CU is important mainly to run the sewerage pump, oil central heating starter and pump, and LED lights. Not necessarily a high load.

All wiring is modern (2018 and 2020) and full RCBOs. All Hager.
 

let the smart meter guy fit the isolator,
after that is done, you are free to take the tails from the outgoing side of the isolator and put it into the changeover switch.
 
Needs a mains isolator AND a change over switch. Isolator to be switched 'off' before C/O switch is turned to 'generator', and left off until after C/O switch is turned back to mains.
Also note that you will have to supply your own earthing arrangements, which will probably be TT.
 
Thanks guys. Very helpful. Yes. I had realised I would need to install a TT earthing system. We already have one for the EV charger, but not in a convenient location. I have two four foot rods in stock and plan to install both a short distance apart using an excavator when I put some footings in.

For a transfer switch I think I prefer not to use a rotary switch as other people can find these confusing and it may not be me operating it. I will obtain an IP68 enclosed switch, and install that outside adjacent to the meter box within another weatherproof enclosure (just to be on the safe side) with a protected permanent socket for the generator (which is in fact 13/32 not 13/16 as I originally typed).

Our energy supplier is Octopus and they are truly hopeless at getting back to us re fitting a smart meter and isolator. The DNO is not interested and there are no seals on the incoming fuse, which they don't appear to care about either.
 
The consequences of the generator 'feeding back' into the mains can be fatal to DNO personnel. A change over switch is required, and the isolator is there to back up that switch in case of failure.
How is a rotary switch confusing, especially if it is labelled 'generator' and 'mains'?
 
  • Like
Reactions: James
It is not confusing to me. However, we have rotary switches on the boiler and sewerage plant isolators and both my wife and (German) in-laws say they find these confusing.

I am aware that feedback must be avoided. I referred to exactly that in my original post.

None of this is an issue if I am around. However, when we had the recent 3 day power outage I was in hospital and despite training and clear labelling ( I produced a laminated start up and connection guide) on the generator, no one was able to operate it. I need to make things very simple to avoid confusion, especially as the users are used to German plant (3 phase in their case) and German labelling (I will do it in both languages in future).
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Isolator vs Transfer Switch for generator (or both)
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
AJB Temple,
Last reply from
AJB Temple,
Replies
5
Views
5,423

Advert