Hi everybody,
I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting cables are clipped to the ceiling and walls, So my question is... do the lighting circuits need RCD protection due to not being 50mm deep in walls and fire proof clips there was none, I cant seem to find the answer. I feel they do because of being surface mounted and fire proof clips for the fire exit routes. What code would you use for these? Many thanks
I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting cables are clipped to the ceiling and walls, So my question is... do the lighting circuits need RCD protection due to not being 50mm deep in walls and fire proof clips there was none, I cant seem to find the answer. I feel they do because of being surface mounted and fire proof clips for the fire exit routes. What code would you use for these? Many thanks