Re Buzzlightyear's #7 - reversed polarity:
I've been mulling over Buzzlightyear's interesting hypothesis . It would have a possible association with the recent swap of consumer unit; before it all was well and afterwards it was not in the lives of kettles. And there is a further consequence of reversed polarity - the wire element will spend most of its life at mains potential which in turn means the insulation around it and encased by the metal casing is permanently subject to mains voltage electric field. This electric field is the same magnitude (240V rms, 350V peak) all along its length. For the brief periods the element is on to heat water, the electric field will be tapered from 240/350V at the line end to 0V at the neutral (and now switch) end. With correct polarity there is no electric field for the vast majority of the day and when used it is only a tapered electric field.
With reversed polarity there would be then a change in the electrical stress on the element and in particular its insulation. Maybe then the insulation is breaking down because of the unusual prolonged mains electric field? eg partial discharge - at a place or places along the wire element? Over time this earth fault current combined with the LN current is high enough to trip the mcb (but which mechanism thermal or magnetic?). Depending on the overcurrent it is not unknown for mcbs to trip before a 13A fuse ruptures.
Partial discharge - Wikipedia - https://en.wikipedia.org/wiki/Partial_discharge
Why most often first thing in the morning? Because at this time the element has spent the longest time energised for partial discharge (or something else) to begin to form a tracking path to earth for a low leakage current to begin with which eventually breaks down under the influence of heat for a significant flow of current. The rcd does not trip (it is stated #1) perhaps because the tracking only causes a small earth leakage current to begin with - though I would have expected both the mcb and rcd to trip when the element's insulation eventually failed catastrophically - so I admit my theory does not fit well if the rcd stays closed.
The long and the short of it then is I would check the polarity of the supply at the socket the kettle normally uses and while at it in the CU too.

[automerge]1581070106[/automerge]
For the Landlord - does the mcb trip when the kettle is first turned on or during the heat cycle?
I've been mulling over Buzzlightyear's interesting hypothesis . It would have a possible association with the recent swap of consumer unit; before it all was well and afterwards it was not in the lives of kettles. And there is a further consequence of reversed polarity - the wire element will spend most of its life at mains potential which in turn means the insulation around it and encased by the metal casing is permanently subject to mains voltage electric field. This electric field is the same magnitude (240V rms, 350V peak) all along its length. For the brief periods the element is on to heat water, the electric field will be tapered from 240/350V at the line end to 0V at the neutral (and now switch) end. With correct polarity there is no electric field for the vast majority of the day and when used it is only a tapered electric field.
With reversed polarity there would be then a change in the electrical stress on the element and in particular its insulation. Maybe then the insulation is breaking down because of the unusual prolonged mains electric field? eg partial discharge - at a place or places along the wire element? Over time this earth fault current combined with the LN current is high enough to trip the mcb (but which mechanism thermal or magnetic?). Depending on the overcurrent it is not unknown for mcbs to trip before a 13A fuse ruptures.
Partial discharge - Wikipedia - https://en.wikipedia.org/wiki/Partial_discharge
Why most often first thing in the morning? Because at this time the element has spent the longest time energised for partial discharge (or something else) to begin to form a tracking path to earth for a low leakage current to begin with which eventually breaks down under the influence of heat for a significant flow of current. The rcd does not trip (it is stated #1) perhaps because the tracking only causes a small earth leakage current to begin with - though I would have expected both the mcb and rcd to trip when the element's insulation eventually failed catastrophically - so I admit my theory does not fit well if the rcd stays closed.
The long and the short of it then is I would check the polarity of the supply at the socket the kettle normally uses and while at it in the CU too.

[automerge]1581070106[/automerge]
For the Landlord - does the mcb trip when the kettle is first turned on or during the heat cycle?