ChrisElectrical88

Hey guys.

just looking for some advice to back up what I have told one of the lads. He wired an emergency lighting circuit with a FP coming into the dist board. He took this FP through the board into the key switch mounted on the side of it then a FP back into the board through the bush and coupler. Still following. Probably not! Anyway apart from pointlessly taking the neutral into the switch he connected the lives through the L1 terminal and the neutral through the L2.

i made him disconnect the neutrals as it was a L terminal as they would not be correctly identified. Also he didn't see the reason why the switch didn't need a neutral.

Point anyway way after this ridiculous post is, would you connect a neutral into a L terminal?
 
2 L1 and 2 L2 terminations, if it was a N termination like every double pole switch iv ever seen it wouldn't have been a issue. Iv even starting to question it been an intermediate key switch.
 
Answer No, neutrals linked, and line in to com, and line out to L1......But why have you wired the installation in FP200..??
 
Answer No, neutrals linked, and line in to com, and line out to L1......But why have you wired the installation in FP200..??
waste of money using fp for emergency lights, they have battery backups.
 
  • Like
Reactions: 1 person
That's a location, not a reason for installing FP, you'd normally expect to see steel pipe in a factory rather than FP
 
Has he specified this in metal trunking along with singles for lighting & power, or are all other cables T&E..?
 
Has he specified this in metal trunking along with singles for lighting & power, or are all other cables T&E..?
im not joing ive been on a site before where everything was wired in fp, sockets, lights etc.

only difference between alarms and everything else was colour
 
im not joing ive been on a site before where everything was wired in fp, sockets, lights etc.

only difference between alarms and everything else was colour
Then there`s the heath & safety aspect, were containment means just that. Contained securely in the event of fire, and not just clip or srewed to walls
 
Then there`s the heath & safety aspect, were containment means just that. Contained securely in the event of fire, and not just clip or srewed to walls
everything was on basket then drops down in either tray or conduit with metal tywraps (no idea why the use of metal tywraps on plastic conduit)
 
Every Specification I have come across, for commercial, schools and offices have all been the same.
Tray for armored, Basket for data/fire/security and box trunking using singles for power lighting. All cables on tray/basket supported by metal ties every 1m, plastic ties every 1/3m. And all drops or surface plant rooms galv conduit. Whole idea here, is to prevent a rats nest dropping on people escaping from a building and firefighter entering a building.Hence the metal ties holding cable on tray/basket.
 
  • Like
Reactions: 1 person

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Key switch
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
ChrisElectrical88,
Last reply from
tazz,
Replies
15
Views
142

Advert