Biffs made a good point, unless it is a huge range I bet the hob and oven can go onto one circuit

- - - Updated - - -

I was just thinking about stealing a cooker circuit, Biff. The hob is 4.7kW, but I don't know what the oven will be.

not much I suspect, allowing for diversity a 6mm2 will do both IMO, and you would have a spare way
 
well even if its a double oven at another 4kw , that gives a total of 8 and a half kw's.
upgrade the mcb to 40a and away you go , 6mm is still fine for both.
 
ask em what the oven is they plan to have (they should already know as they will have designed the kitchen area already).......then look it up....
 
That will only leave the challenge of fitting 6mm conductors into a UFH controller! Or an FCU, that won't be so bad. :)
 
You've so many options you can now choose the best option for your actual circumstances! Can't be bad eh? :)
 