There not exemptions.
The requirement as I've probably mentioned on more than a few occasions, is for RCD protection to be provided for socket-outlets for use by ordinary persons and that are intended for general use.
If sockets are not for use by ordinary persons, or not intended for general use, there is no requirement for RCD protection.
pThe reason why we have this requirement for RCD protection for socket-outlets, is because they are used to connect mobile (as in hand held) equipment.
Such equipment is more prone to damage than static equipment, cords, cases and even the plugs and sockets can easily be damaged.

Im not disagreeing with you spin i just IMHO believe that rcd protection in domestic should now be fitted regardless except for exceptional circumstances and most cases domest will have cables within 50mm of the surface as surface mount gear isn't really appealing in your home, so the install method alone 9/10 times will give requirements for an rcd, to meet all the exceptions to omit rcd in domestic now is uncommon unless purposely done so, ive done several kitchens all fully rcd/rcbo covered since 17th and not yet had any issues with nuisance tripping, also found a brand new washer needed returning due to faulty smoothing cap' ....this wouldn't have shown up on a none rcd circuit because we tried but the interference from the motor could have played havoc with other sensitive equipment in the house as the cap' had failed but not shorted. For this and similar reasons including added safety i rcd/rcbo protect all domestic when i can.
 
The T&E was the main supply cable run from a s/f unit in the intake cupboard within the communal hallway. The main earthing conductor was noted within the departures box on the cert as being 6mm2 confirmed for adequacy using adiabatic calculation in accordance with table 55.3 & reg 543.1.3
 
In the departures box, or the 'comments on existing installation' box?

What's going on with the nulls apearing when someone is quoted, another glitch?
 
well..just been reading the first page of this....
work out what the max. demand is likely to be within the kitchen....then work from there....
pretty standard isn`t it...
 
In the departures box, or the 'comments on existing installation' box?

What's going on with the nulls apearing when someone is quoted, another glitch?
It was noted in the comments box. At first glance i thought....hang on new board and bonding but not uprated the main earth? When i saw the route involved and probably the rates they were working to i could see why it was left. They used the equation which i confirmed as being accurate. Apparently they had some D.I in stating the earth was to small and should not have been certified so i was just questioning my own judgement and application of the regs on this matter.
 
here in the US when we install any ckt's in a kitchen, washroom, or bathroom they must be protected by a gfci (ground fault circuit interrupt)
these devices will trip out a circuit before any shock happens
although im not sure what they are called in the UK.
for my customers protection i make this an absolute must
 
Its a kitchen Spin in an house i dont think we should be even looking for exemptions to rcd coverage .... rcd all the time in domestic regardless and i would argue anyone trying to express exemptions, well i assume on of the sockets isnt for a kidney Dialysis machine then il back down ;) ....

Houses are the biggest place of electrical acidents, old people, children etc make it a risky environment and now we have the means to make it safer we should do whenever we can.

Did a huge domestic kitchen job a while back....big american style fridge/wine chiller and the manufacturers instruction clearly stated 'RCD not recommended'.....The beast needed 2 single sockets, we installed as 2 radials off 16a mcb's with the drops in steel conduit.
 
Did a huge domestic kitchen job a while back....big american style fridge/wine chiller and the manufacturers instruction clearly stated 'RCD not recommended'.....The beast needed 2 single sockets, we installed as 2 radials off 16a mcb's with the drops in steel conduit.

Ive heard this before ... i believe the manufacturers were inundated with earth leakage issues of their fridges (possible design flaw, cant remember the conclusion) so rather than address the issue they just added a paragraph to the installation bumf, youll probably find their future models don't have this clause but yeah a bummer when your forced to put steel drops in or mechanically protected cable. I always segregate freezers etc with rcbo and so far every customer has been happy to folk out the extra to do so. (even though as spin points out i could get away without protecting it if im not having cables <50mm to surface)
 
here in the US when we install any ckt's in a kitchen, washroom, or bathroom they must be protected by a gfci (ground fault circuit interrupt)
these devices will trip out a circuit before any shock happens
although im not sure what they are called in the UK.
for my customers protection i make this an absolute must

Don't tell them that you also install socket outlets in your bathrooms!! ...lol!! You'll get a load of tosh, telling how dangerous this is!! ..lol!!:smilielol5::cowboy:
 
Did a huge domestic kitchen job a while back....big american style fridge/wine chiller and the manufacturers instruction clearly stated 'RCD not recommended'.....The beast needed 2 single sockets, we installed as 2 radials off 16a mcb's with the drops in steel conduit.

Manufacturers are full of kak. How can they run around saying 'RCD not recommended just because of their poor design and manufacturing standards. There's no reason in this day and age that any kitchen appliances shouldn't be capable of being installed on an RCD protected supply.
 
Manufacturers are full of kak. How can they run around saying 'RCD not recommended just because of their poor design and manufacturing standards. There's no reason in this day and age that any kitchen appliances shouldn't be capable of being installed on an RCD protected supply.

Very true!! Just depends on, what other loads are on the fridge/freezer circuit though. A separate RCBO radial circuit shouldn't be any problem what-so-ever!!
 
Manufacturers are full of kak. How can they run around saying 'RCD not recommended just because of their poor design and manufacturing standards. There's no reason in this day and age that any kitchen appliances shouldn't be capable of being installed on an RCD protected supply.

Very true!! Just depends on, what other loads are on the fridge/freezer circuit though. A separate RCBO radial circuit shouldn't be any problem what-so-ever!!

The two single sockets were on dedicated radials and directly above the appliances and labelled,so highly unlikely to be used for anything else......As far as I'm concerned if manufacturer states 'no RCD' I'm not putting one on,'cos if I do and the client gets back from his fortnight in florida to a fridge full of maggots I'm going to have some explaining to do.
 
Don't tell them that you also install socket outlets in your bathrooms!! ...lol!! You'll get a load of tosh, telling how dangerous this is!! ..lol!!:smilielol5::cowboy:

this is why we use the gfci. both the socket type and whole house type
also many portable devices including some washers and dryers are being equipped with them in the plug.
heres the wiki on them
http://en.wikipedia.org/wiki/Residual-current_device
in the uk i guess they are called rcbo's
 
To the Op its always worth doing a bit of testing on the ring you are adding to before you do, any problems with it run in a new circuit save you no end of grief like, open end to end readings with the break somewhere in the house , Zs too high etc , I assume you'll be completing the certificates yourself

Sounds to me like the previous bloke was quick (as he was doing less than he should have) which translated into manager speak means he was good at his job ! and I'd bet the paperwork was iffy or nonexistent.
 
this is why we use the gfci. both the socket type and whole house type
also many portable devices including some washers and dryers are being equipped with them in the plug.
heres the wiki on them
Residual-current device - Wikipedia, the free encyclopedia
in the uk i guess they are called rcbo's

We use RCBO's and RCD's, but you won't convince many here to install a socket outlet in a bathroom!! They have been brainwashed over many years now, No socket outlets in a bathroom, only SELV shaver outlets, that they also want to see protected by an RCD, (why i have no idea)!! ...lol!!
 

OFFICIAL SPONSORS

OFFICIAL SPONSORS

Thread statistics

Created
Matesrates,
Last reply from
Engineer54,
Replies
61
Views
5,553
Back
Top