D
Darkwood
There not exemptions.
The requirement as I've probably mentioned on more than a few occasions, is for RCD protection to be provided for socket-outlets for use by ordinary persons and that are intended for general use.
If sockets are not for use by ordinary persons, or not intended for general use, there is no requirement for RCD protection.
pThe reason why we have this requirement for RCD protection for socket-outlets, is because they are used to connect mobile (as in hand held) equipment.
Such equipment is more prone to damage than static equipment, cords, cases and even the plugs and sockets can easily be damaged.
Im not disagreeing with you spin i just IMHO believe that rcd protection in domestic should now be fitted regardless except for exceptional circumstances and most cases domest will have cables within 50mm of the surface as surface mount gear isn't really appealing in your home, so the install method alone 9/10 times will give requirements for an rcd, to meet all the exceptions to omit rcd in domestic now is uncommon unless purposely done so, ive done several kitchens all fully rcd/rcbo covered since 17th and not yet had any issues with nuisance tripping, also found a brand new washer needed returning due to faulty smoothing cap' ....this wouldn't have shown up on a none rcd circuit because we tried but the interference from the motor could have played havoc with other sensitive equipment in the house as the cap' had failed but not shorted. For this and similar reasons including added safety i rcd/rcbo protect all domestic when i can.
....