Just hoping to get a second opinion before i submit an EICR i carried out on a Launderette .

All the isolators for the machines are hidden behind and accessible by removing a wooden panel that sits on top but any customers are unlikely to know this unless the owner is in constant supervision and ready to isolate if required in an emergency .

Looking around at other Launderettes this seems to be common practice but not ideal , im struggling wether tho give it a C2 or 3 as it has been operating for 40 odd years and the circuits are in good condition with all earthing etc .

Opinions please ?

Lee
 
Hi Stspark

Thanks for the reply , If something was to go wrong with the machine and it needed to be isolated then I would expect the isolator to be readily available but maybe I’m being over cautious with it being accessed by the public .
I know it’s my call but what would you code it or not as the case may be ?

Thanks
 
If the isolator was required to stop the machine in an emergency would it not be a emergency stop switch?

Or are these local isolation points?
 
No code, its not emergency swotching in my opionion. Only code if inaccessible for mechanical maintenance IMHO
 
Thanks Strima

Fair point they are local isolation switches rather then emergency was still thinking they should be easily accessible but I guess as long as the owner knows where to isolate from if needed it should be fine
 
Thanks Chris

Defo being over cautious with my thinking and really appreciate the advice .
 
I would imagine they're hidden to stop people deliberately turning them off, apparently some people are just stupid and want to cause annoyance to others.

If there was a master emergency stop, people would push that as well.
 