Hi Guys

Just hoping to get a second opinion before i submit an EICR i carried out on a Launderette .

All the isolators for the machines are hidden behind and accessible by removing a wooden panel that sits on top but any customers are unlikely to know this unless the owner is in constant supervision and ready to isolate if required in an emergency .

Looking around at other Launderettes this seems to be common practice but not ideal , im struggling wether tho give it a C2 or 3 as it has been operating for 40 odd years and the circuits are in good condition with all earthing etc .

Opinions please ?

Lee
 
Hi Stspark

Thanks for the reply , If something was to go wrong with the machine and it needed to be isolated then I would expect the isolator to be readily available but maybe I’m being over cautious with it being accessed by the public .
I know it’s my call but what would you code it or not as the case may be ?

Thanks
 
If the isolator was required to stop the machine in an emergency would it not be a emergency stop switch?

Or are these local isolation points?
 
Thanks Strima

Fair point they are local isolation switches rather then emergency was still thinking they should be easily accessible but I guess as long as the owner knows where to isolate from if needed it should be fine
 
I would imagine they're hidden to stop people deliberately turning them off, apparently some people are just stupid and want to cause annoyance to others.

If there was a master emergency stop, people would push that as well.
 

Reply to Launderette EICR advice please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Many of you have been assisting me with a different EICR issue. Your contribution has been invaluable. This post is not related to that...
Replies
32
Views
5K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G
I went to a job that the owner felt was a bodged job. It was basically a radial circuit wired at the start in 4.0mm T&E, and then it goes to a few...
Replies
27
Views
3K
Helpful and constructive advice only please. I appreciate this inquiry isn't ideal. As a mainly petrochemical Sparky I've been asked to help a...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock