Are you doing an EICR or fault finding.
Is this 130 and 150 ohms or meg ohms.
Are you registering voltage between line/earth at the light fitting and is the insulation resistance clear.
Yes 130 meg ohm for IR.It isn't a problem I thought you meant ohms for when the switch was open. I assume you get 130 meg ohm when you IR test the whole circuit with all switches closed.
Are the switches relatively old as you could be getting dirt on the contacts at the switch tracking across or you may have leakage through lower insulation resistance