I think they will need to be separated to help the reduction in inrush
Use the switched live to feed the contactor coil and one half of the lights and use a permanent live to feed the other half via the switching contacts of the contactor
This is a option to reduce the inrush
 
try a C10 if the Zs is low enough.
 
You may find your switch gets damaged over time though. As has been said a current limiter prior to the switch is the more conventional method of dealing with inrush currents. Contactors, relays and switches are all in line of the inrush and will suffer over time. I hope with the C curve MCB you have taken account of the ADS and max Zs that it meets required disconnection times? There is much evidence of fusing and meltdown of contactor, relays and switches in such circuits.
 
I’m am at the property now and have put a c10 mcb in and all seems good have tried them over 50 times and no tripping
upload_2017-11-21_16-31-31.png
 