Hi E.F.
I am replacing 3 lighting transformers in my kitchen.
The existing ones plug into 3 x main sockets which are on the AC mains circuit via a light switch and are earthed.
The replacement transformers have no earth connection - do I need to earth the new transformers? If so, how?
It's a DIY project, any pointers appreciated.
Thanks,
Simon
Manchester
 
Does the new transformer have a logo, a square within a square? if yes then it's double insulated and doesn't require a cpc.
 
upload_2018-10-8_13-41-40.png
 
Hi E.F.
I am replacing 3 lighting transformers in my kitchen.
The existing ones plug into 3 x main sockets which are on the AC mains circuit via a light switch and are earthed.
The replacement transformers have no earth connection - do I need to earth the new transformers? If so, how?
It's a DIY project, any pointers appreciated.
Thanks,
Simon
Manchester

God help us all
 
plenty electricians in manc area could wire this up properly 4u. lights fed from 3 13A plugs via light switches is so Romanian.
 
Hum ..... lighting transformers in 13A sockets ..... op could you post a picky of the new transformer ?

And why not a like for like replacement?
 
Hi Murdoch,
The previous transformers were Ikea mains plug transformers, all goosed.
I've attached a grab of the transformer I've bought.
Thanks,
Simon
TRAN.jpg
 
That's a class 2 transformer so doesn't need an earth .....
Thanks Murdoch - I've wired the new transformer up and it works. What do I do with the earth cable that was wired into the mains socket?
Cheers, Simon
 