Hey guysI've been tasked by my supervisor to carry out earth electrode testing on the lightning protection systems of two buildings we maintain. Nothing to difficult. Carried out 4 pin test on all down conductors. Got all my results. He's asked me to put into a proper format much a kin to that of schedule of test results. However I can't find any official paperwork or test results forms. Does anyone know if they do actually exist and if so, does anyone have a copy of them I could use please. Thanks very muchLex
 
So who's doing the rest of the lightning protection systems PIR testing and inspections??

Sorry can't help you with test sheets etc, but you will find there is a general format for inspections of lightning protection systems in the UK, which will be similar to EICR (or whatever it's called now). It will want to know a dam sight more that just the down conductors earth electrode values.

EDIT....

By the way, 4 pin testing as you call it, is normally used to measure the resistance value of the soil, rather than the electrode. Though you can still use a 4 pin test procedure for testing the electrodes. Just that the maths start to get a bit involved!! lol!!
 
Last edited by a moderator:
Hi mate, I'm an L/c engineer, I don't think there is any general format test result sheets, I've seen some test Certs that look like they been written on word, you need to make note of any plant or metallic structures that arnt bonded back to the system. ie; aerial within 2m of a conducter aircon units and so on. You should test all positions by disconnecting at the test point test the electrode. The test value of the building should be less that 10 ohms. So if you building had 6 conducters the value of each earth should be no greater than 60 ohms then combined it would be less than 10ohms, continuity testing is always worth while too test from conducter to conducter testing with a fly lead, then test resistance of fly lead subtracting that from you reading, that tests up and over the system, with the leads subtracted it the value should be no greater than 0.3 ohms, I'm a little bit rusty on testing hope it helps
 
Cheers that's grand. I've done continuity testing between conductors and whole system tests. So far its all passed. Will just have to make up my own result sheets now.
 
If there isn't a general format inspection/test report certificate used in the UK these day's your best bet is to contact a company specialising in LP and see what they produce.

Another thing is any continuity tests conducted across individual joints or even sections/parts of the air conductor system needs to be conducted with a resistance tester capable of testing with a current of at least 10A (Ductor). A typical MFT which uses around 100/200mA test current, is just not capable of giving you any realistic values over such a mass of hard drawn copper.

Again there is a lot more to a LP system that needs checking and testing, far too much to list here. None of it's what anyone would call Rocket Science, but it all needs to be done just the same...
 
Last edited by a moderator: