Hi Boydy,
The install is TT with Ra of nigh on 60 ohms. Was not really expecting a PD of 230V between rod and neutral. Maybe the fault is L-CPC rather than N-CPC. Need to investigate further, though I think the client prob thinks I am spinning them a yarn as only went there to fit an extra light fitting. Now they need a new earth and RCD protection!
I left the circuit isolated and will ring them tomorrow to see whats what!
in answer to your qu I have checked some Zs's out of curiosity on other circuits, and they are all around 20 ohms with water bond in place (no gas there). So the earth is not the best at present.... but did not check other circuits for N-CPC voltage, no.