- Reaction score
- 10,220
To be fair and I have touched on this, I would require a hell of a lot more info of Lee before designer the motor power supply, like I said, even something as simple as having speed control could change the requirements of the existing motor set-up and could require the need for force ventilation.
VSD - Motor cabling also has many factors to be considered here, the BS7671 is based on general cables and their common ratings and values, if you come away from these and go into specialised cabling with different insulation and sheath materials then it can open other options which can see reduction in CSA, I use IGUS and LAPP brands which can mean you have to forget the BS7671 charts and use the manufacturers guides.