When you say it was fine, what was fine each radial between L/N or the supply to the shed board.did break it down the radial and lights was fine
When you say it was fine, what was fine each radial between L/N or the supply to the shed board.did break it down the radial and lights was fine
did the l-n to each circuit after removing from the board, just low when connected to the board, when testing the whole board l-nWhen you say it was fine, what was fine each radial between L/N or the supply to the shed board.
yes mate trust me completely confusedWell it shouldn't be, have you got the switch off at the board.
no mateyour not testing at the main incomming terminals of the main switch
yes rcdI take it the board has a rcd main switch it could be reading across that. Switch off the MCBs and take the supply neutral from the neutral bar.
Ok so it's a personal preference then?