hi did a IR on a shed board L-N was 0.11Mohms so took out the radial circiut and light circuit did them separately and was fine 299Mohms so why low when they are connected to the shed board????? dont do much testing so help be nice cheers
IR tests should be carried out with L and N dissed from the board, so that low reading is irrelevant.
Hi Tel don't normally question your replies, but looking at table 10.3.3 in the OSG it says.
"For an installation operating at 400/230V , although the IR value of 1Mohm complies with BS7671, where the IR reading is less than 2Mohm the possibility of a latent defect exists. in these circumstances each circuit should be tested separately" The original test was obviously a global test at the board.
Why were you testing the shed?
Surely you must have seen a difference at some point!
Does the shed have a cu and if so what type? What is at the house end of the circuit? How many circuits in the shed?
I take it the board has a rcd main switch it could be reading across that. Switch off the MCBs and take the supply neutral from the neutral bar.
Just the way I do it - thoroughly.
In this case it would have saved time and I'm personally not keen on the linked live to neutral test either
Where practicable I always test the entire dis. board in parallel. As stated RCBOs can make that impracticable.
But either way we need to consider the effect of the results in parallel, as the minimum values of insulation resistance quoted in BS 7671:2008 (2015) are for the whole installation, or in larger installations a distribution board with all final circuits connected in parallel. They are not minimum values for a single final circuit.
It would not have been the end of the world,to test at the neutral bar/MCB's,while the circuits were disconnected,and work out where this reading originated from,including any issue with the actual board.
I could not have left,before answering my own question ;)
Reply to low IR in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...