davesparks
I don't think that works. Typically most meters are specified as something like +/-X% + N digits, your X percentage is the same on the total, once you remove the added R and its known range you get an even wider percentage of the result. Similarly once your R is subtracted from the reading, you still have the N least digits to consider.
Sadly none of the MFT I have ever seen even have the option for Kelvin cables, even as extra-cost option, which would get rid of a bit of the low R uncertainty at relatively low cost.
Yeah I have never been too certain of the method either but it was championed by the late Engineer54, you could probably find his posts on the subject with a bit of searching.