Having to re cable the lighting in a metal portacabin,the cabin is placed in a workshop,would you main bond it,doubts due to new 18 th edition,on the requirements of main bonding.
The cabin is not an extraneous conductive part,& will be earthed fortuitously by the lighting equipment.
 
Having to re cable the lighting in a metal portacabin,the cabin is placed in a workshop,would you main bond it,doubts due to new 18 th edition,on the requirements of main bonding.
The cabin is not an extraneous conductive part,& will be earthed fortuitously by the lighting equipment.
What with a Crabby 1mm2 cpc, cosmic
 
The requirements as to whether the cabin needs bonding are no different from the 17th Ed to the 18th Ed. Nothing has changed.
 
Im looking @ it,with these new regs,on bonding,it states that if it’s a plastic insert,on incoming pipes,then no bonding required.
This includes all other pipework that is relevant to that system,it does not need bonding.
With that in mind,the Cabin isn’t extraneous & so does not require main bonding,but earthed locally by cpc of the equipment inside.
 
I doubt it requires protective bonding unless the cabin has its foundations anchored or bolted through the flooring membrane and in good contact with the general mass of earth below.
 
It can’t be an extraneous conductive part,cause it’s inside the building.
Why bond it when there’s no need to bond metal pipes in situ,if they have a plastic insert @ entry to that building .
 
It can’t be an extraneous conductive part,cause it’s inside the building.
Why bond it when there’s no need to bond metal pipes in situ,if they have a plastic insert @ entry to that building .
You could say that about any metalwork within the building that may or may not be classed as extraneous.
 
We’ll need 3 dozen buckets of popcorn and around 7 tin hats - STAT!
 

Reply to Main bonding to do or not to do in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
622
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
731
Probably a basic question In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock