Hi all, thanks in advance for any helpful comments.
Ive just completed a fuse board change to a flat above a shop. They both have there individual cut outs.
( I also installed main protective boding as there was none is place)
went to do continuity of main earth which I could see at the board, as the cut out was right next to the board I thought this should be easy, except it was not there. So maybe it's a TT? So I completed all other dead tests, all circuits fine. Put board together.
(I rang the dno they insist there is no PME in the area)
I then carried out a ZE Which gave me 0.13 thinking this is pretty good to be a TT I thought this must come from down stairs it appears to the way it goes through the ceiling.
Any how went down to the shop but the owner will not let me have a look, I thought, unhelpful. I rang the dno again and they are going to come down for an investigation hopefully forcing the owner into letting us in.( well not force but you know what I mean)
So what is the position I can leave this installation in? I have no PME except I have a decent earth and in all sense and purposes is very safe.
Thank you for good comments will answer any questions and the end of the working day.
Ive just completed a fuse board change to a flat above a shop. They both have there individual cut outs.
( I also installed main protective boding as there was none is place)
went to do continuity of main earth which I could see at the board, as the cut out was right next to the board I thought this should be easy, except it was not there. So maybe it's a TT? So I completed all other dead tests, all circuits fine. Put board together.
(I rang the dno they insist there is no PME in the area)
I then carried out a ZE Which gave me 0.13 thinking this is pretty good to be a TT I thought this must come from down stairs it appears to the way it goes through the ceiling.
Any how went down to the shop but the owner will not let me have a look, I thought, unhelpful. I rang the dno again and they are going to come down for an investigation hopefully forcing the owner into letting us in.( well not force but you know what I mean)
So what is the position I can leave this installation in? I have no PME except I have a decent earth and in all sense and purposes is very safe.
Thank you for good comments will answer any questions and the end of the working day.