Can the main earth be run on the outside of a building from the MET to the consumer unit clipped direct?

Would it not need some form of protection
 
Black plastic conduit may well provide adequate protection, but all the regulations relevant to the particular installation will need to be complied with. Unfortunately if you are looking for a reg which states ' main earth wires shall not be clipped direct externally' you wont find it.
 
If it is something you are planning to install then I would suggest some outdoor-rated conduit. Black usually is, but you may find other colours are also UV stabilised.

It might not need protection strictly by the regs, but you have to take in to account the risk of physical damage from accidents like wheely bins knocking it, or the local scroats nicking it as it looks like enough copper to buy a beer.
 
If it is something you are planning to install then I would suggest some outdoor-rated conduit. Black usually is, but you may find other colours are also UV stabilised.

It might not need protection strictly by the regs, but you have to take in to account the risk of physical damage from accidents like wheely bins knocking it, or the local scroats nicking it as it looks like enough copper to buy a beer.
Black Plastic conduit or would it have to be metal conduit its for my flat it would be at minimum two meters from the ground
 
no problem just to clip it direct onto the wall. or could get british gas to just throw it from one point to the meter, just 20ft.of 10mm Gn/Y dangling.
 
no problem just to clip it direct onto the wall. or could get british gas to just throw it from one point to the meter, just 20ft.of 10mm Gn/Y dangling.
Lol?

Its the main earth thats 16mm i have sorta understood that anything above 4mm can doesnt need mechanical protection even if its the main earth going to the MET in an out house type building where the incoming is

But conduit couldn't hurt right ?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Main earth run outside?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
dokkan1080,
Last reply from
dokkan1080,
Replies
15
Views
2,444

Advert

Back
Top