Good Eveing to you all,
Came across this installation today , iam just running new ring in the kitchen off the original board main switch 80A RCCB 30mA, 15TH ED MEB, PLUS MAIN EARHT SOILD GREEN SLEVEING,
BEFORE I START IAM GOING TO UP GRADE MEB TO 10MM,, HERES WERE IAM IN A BIT OF LIMBO,, ON CHECKING MAIN EARTH FROM CUT OUT FUSE (SYSTEM IS TN-C-S) WHIT A NEW DIGGY METER BEEN INSTALLED,,, THEY HAVE BROUGHT 16MM CPC FROM THE MAIN FUSE ABOUT 500MM LONG AND CONNECTED IT TO CPC FEED BOARD IN OUTSIDE METER BOX ,USING A CONNECTOR BLOCK ,,
NOW,,,, DO I CHANGE THE PICE FROM CONNECTOR BLOCK TO 16MM BACK TO THE BOARD
DO I PHONE ELECTRICAL BOARD AND ASK ABOUT METER CHANING PEOPLE ABOUT STANARDED
OR JUST RENEW MAIN MEB AND REPORT THE DOGGY WORKMANSHIP TO ELECTRIC BOARD
ANY REPLY WELECOM
Came across this installation today , iam just running new ring in the kitchen off the original board main switch 80A RCCB 30mA, 15TH ED MEB, PLUS MAIN EARHT SOILD GREEN SLEVEING,
BEFORE I START IAM GOING TO UP GRADE MEB TO 10MM,, HERES WERE IAM IN A BIT OF LIMBO,, ON CHECKING MAIN EARTH FROM CUT OUT FUSE (SYSTEM IS TN-C-S) WHIT A NEW DIGGY METER BEEN INSTALLED,,, THEY HAVE BROUGHT 16MM CPC FROM THE MAIN FUSE ABOUT 500MM LONG AND CONNECTED IT TO CPC FEED BOARD IN OUTSIDE METER BOX ,USING A CONNECTOR BLOCK ,,