Discuss Main Earthing Conductor Termination with SPDs in the UK Electrical Forum area at ElectriciansForums.net
Strima
Here's a question that I was asked earlier.
If you have SPDs installed in a DB is it permissible to terminate the main earthing conductor into the SPD first then the DB earth bar?
Or must it be terminated in the DB earth bar first then the SPD?
I have always terminated to the MET first and then taken a suitably sized CPC from the SPD to the MET.
This means you can replace the SPD without disconnecting the main earth for the installation.
Never fitted them in a domestic situation, only in motor control centers.
Its probably not necessary to run a 16sq earth to the SPD in a domestic installation so best do as Rob says, and a smaller link (4sq mm?) to the SPD.