Guest123
If they supplier hasn't supplied an earthing facilty from the off, they are under no obligation to provide you with one now.
The way I see it, the customer either pays you £400 odd for a suitable Cu upgrade or £3000 to the DNO to PME their system and supply you with an MET.
Kind of a no brainer to me.
Apologies if I have the wrong end of the stick though.
The way I see it, the customer either pays you £400 odd for a suitable Cu upgrade or £3000 to the DNO to PME their system and supply you with an MET.
Kind of a no brainer to me.
Apologies if I have the wrong end of the stick though.