any isolator up front before the new c/u does not require a metal ,
but if you are happy ,then go for it ,
Well, I respectfully disagree.
When I had a dilemma about this previously, I asked WPD about it and why they fit plastic regardless... the only reason I was given was because they weren't working to BS7671.
Whilst a single isolator may not constitute a type tested arrangement of equipment like a distribution board, personally I feel a metal enclosure for this job offers a better chance of proving I took all reasonable precautions to ensure the safety of the installation should the unthinkable happen. I like to sleep at night.
I've looked at standards for the REC2S isolator... even the Wylex documentation for it doesn't specify any standards to which it complies. However, the REC2S features a standard 2 pole isolator to BS EN 60947-3, so yes, my arrangement will meet that standard because I'm using a standard BS EN 60947-3 double pole 100A isolator. In terms of the seals that are present on a REC2S enclosure, since these are on the metered side of the supply, the seals serve little purpose other than to prevent access for the uninitiated.
If there is a standard which defines what a supply isolator should be, then I'd like to know what it is please
As for terminations... I would like to see double screws return as it's far to easy to loosen a cage clamp. I typically flatten the tails with pliers, tighten them, wiggle, retighten and then periodically check them as I work on the board. I always check them when I'm inspecting and testing and this has revealed numerous loose terminations (including a 40A cooker circuit which miraculously had not suffered any overheating).