537.2.1.1 could te;ll me im wrong[/QUOTE

that's more applicable to individual circuits rarther than the whole installation. look atr 537.2.2.1. both L and N conductors are "live".
 
Last edited:
yours or mine?
 
ok im happy to go with 537.1.4, so would you code this a c3 as must of been fine when installed 19 yrs ago
 
Well u can't say it's a c1 and c2 if it was acceptable when installed

Yes you can, otherwise you will be passing dangerous installations as satisfactory!

An EICR is an assessment of the safety of an installation for continued use which uses the current version of bs7671 as the standard of safety against which the installation is judged.
If an item is immediately dangerous then it is coded C1, if an item is potentially dangerous it is coded C2 both irrespective of whether it complied at the time of installation or not.
Safety improvements which could be made are recommended via the C3 code, this often relates to items which complied with previous regulations but improvements are now possible.
It is not a report on absolute compliance with the current regulations which is why it must not be used to certify new work.

Fused neutrals, bare conductors in wooden trunking, open fronted switchgear, bare busbars insulated by paint only, live parts accessible without the use of a key or tool were all permitted once upon a time, but all get coded.
 

Reply to Main switch in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock