Just out of interest could western powers problems have caused this and would it be possible in any way for this to contribute to the fire.
JUST STARTING TO GOOGLE.
 
all kneel before the mighty instr. tech. !

;-)

Finally, some acknowledgement of my mightiness!!!

kneelsuckers.gif


Instuments, just one of my many skills :)
 
Put simply if you lose the connection to the star point then you lose the neutral,so on a 3 phase system imagine you had a socket fed off red phase and neutral and another from yellow phase to neutral if you lost the main neutral then the neutral bar in the dis board effectively links the sockets on red and yellow phases,so instead of each socket getting 230v they end up getting 415v and bang goes anything thats connected to them.which is why when working on a 3 phase system you should NEVER remove a neutral link with the supply energized.
 
Thos sound like a fault on one of the phases to earth, the fault being a high impedance earth fault. This in effect drops a voltage accross Rb of the Tx. Test to true earth with a large screwdriver.
 

Reply to MAJOR problem with supply... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
554
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock