If I have a fault like that I will normally work until I have at least found it and made any temporary repairs necessary to get the lights back on. But then I am not afraid to work past 'finishing time' and will happily work as late as the client wishes me to in order to get a job done.

Also why was the 'upgrade' to RCBOs required? Did the client request this be carried out after you had carefully talked them through this? I'm sure you didn't just sell it to them as bring a necessary upgrade because the regulations say you have to, because as we all know that's not true!
 
  • Like
Reactions: 1 person
Thanks for most of the replys it ended up being a squished cable in the loft from a walk board on to and the c/u was not up to date to the 17 th edition 7671 so replaced with rcbos.tested dead and live test all performed and passed and certified and logged on to building control .so there won't be any house fires reported from Faversham .I thought I was on a site where I could talk to people in confidence without having the **** taken .I was wrong with my fault finding procedure I shouldn't of tried the mcb with a fault in the circuit but before I left I made sure it was all completely 100% safe hasn't any of yous been on a job and had to leave it and come back the next day with a clearer head obviously not cos you are all pefect.so thanks for your input keep it up north a .

Good lad - well done!!

We had every faith in your ability and knew you would get there in the end!!

Now just get a towel and dry behind your ears and then grow a thicker skin. :)
 
  • Like
Reactions: 4 people
Thanks for most of the replys it ended up being a squished cable in the loft from a walk board on to and the c/u was not up to date to the 17 th edition 7671 so replaced with rcbos.tested dead and live test all performed and passed and certified and logged on to building control .so there won't be any house fires reported from Faversham .I thought I was on a site where I could talk to people in confidence without having the **** taken .I was wrong with my fault finding procedure I shouldn't of tried the mcb with a fault in the circuit but before I left I made sure it was all completely 100% safe hasn't any of yous been on a job and had to leave it and come back the next day with a clearer head obviously not cos you are all pefect.so thanks for your input keep it up north a .


Went to fix a fault, and managed to persuade customer to upgrade a perfectly fine DB to the "17th edition". well done.
 
  • Like
Reactions: 2 people
I explained to the customer about the difference between rcbos and 17th edition d/b and the customer agreed on the rcbos.on the old d/b all the lighting was not protected a shed supply and cooker supply also was not protected by 30mA rcd .Any cables buried less 50mm has to be protectected by a 30mA rcd or rcbo,tt earthing arrangement zs=8.69 ohms thanks to all
 
nothing wrong with explaining the advantages of upgrading the CU and letting customer make an informed decision, as long as you don't do a BG , telling them the old CU is illegal and dangerous.
 
nothing wrong with explaining the advantages of upgrading the CU and letting customer make an informed decision, as long as you don't do a BG , telling them the old CU is illegal and dangerous.
So a 16 th edition c/u is perfectly safe then on a tt earth arrangement ??? What about the earth fault loop impedance being to high to provide the correct disconnection on the circuits not protected by a 30mA rcd ??
 
So a 16 th edition c/u is perfectly safe then on a tt earth arrangement ??? What about the earth fault loop impedance being to high to provide the correct disconnection on the circuits not protected by a 30mA rcd ??


Well it met compliance with the Reg's for far more years than it hasn't!!

Also, are you aware that SP RCBO's are NOT recommended for TT system earthing? They need to be either SP + N RCBO's or DP RCBO's!!
 
  • Like
Reactions: 3 people
Well it met compliance with the Reg's for far more years than it hasn't!!

Also, are you aware that SP RCBO's are NOT recommended for TT system earthing? They need to be either SP + N RCBO's or DP RCBO's!!

Schneider RCBOs explicitly state, they should not be used on TT or IT systems.
 
  • Like
Reactions: 1 person
It would be interesting to know what has been fitted.

The trouble nowadays is RCBO’s being peddled as the instant cure all for all ills. A lot more effort should be made so that people understand the shortcoming of SP RCBO’s.
 
It would be interesting to know what has been fitted.

The trouble nowadays is RCBO’s being peddled as the instant cure all for all ills. A lot more effort should be made so that people understand the shortcoming of SP RCBO’s.
Explain then, I fitted proteus sp rcbo 30mA, I always thought that rcbos are the best protection to have in domestic due to it being less disruptive to other circuits if a fault occured. I'm sure your gonna have a lot to say about this
 
Last edited by a moderator:
Ive just bought a double pole RCBO. Thats the size of an MCB also.

just to have a look at it.

i suspect its like the French ones I've seen in mobile homes
 
Explain then, I fitted proteus sp rcbo 30mA, I always thought that rcbos are the best protection to have in domestic due to it being less disruptive to other circuits if a fault occured. I'm sure your gonna have a lot to say about this


Lose the attitude bonny lad. You're WELL out of your depth and it's showing!
 
  • Like
Reactions: 4 people
Is that a regulation in bs 7671 that sp rcbos are not recommended on a tt system if so what page number is it
 
Single pole rcbo will operate in the event of an N-E fault but will not clear it, I'm sure you can how this can be a problem. Split board with 2x 30ma RCDs will cover all circuits and disconnect both L+N on the affected circuit in the event of a fault.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mcb keeps blowing on lighting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
74

Advert

Thread statistics

Created
Wayne Hudson,
Last reply from
Tuttle,
Replies
74
Views
7,705

Advert