Discuss MCBs for Inverter-Supplied System in the UK Electrical Forum area at ElectriciansForums.net

Phil1234

DIY
Reaction score
0
My house is off-grid and supplied from an inverter. Max power output of the inverter is about 6kW (25A). Max fault current is 100A. The highest rated Type B MCB that can be tripped by this max fault current is 16A, so I cannot use MCBs with higher ratings than that. I cannot have a circuit with loads totalling more than 16A even though the inverter can supply the power. Is there any way around this? Is it acceptable to run an MCB above its rated current? Any ideas would be appreciated!
 
You have three options, the first is to split all loads into smaller 16A radials, so you can distribute it, however this would realistically have to be at the inverter not at a distribution board/cu.

If you can get an older type 1 mcb which has a lower instantaneous trip, then you could use a 25A mcb, alternatively if you obtain manufacturer's data for a type B, careful selection would give you a 20A mcb which will operate within time on 100A.

Lastly, it is permissable to use a rcd/rcbo if the fault current is insufficient, however you need to ensure the inverter is correctly earthed and can provide earth fault current.
 
You have three options, the first is to split all loads into smaller 16A radials, so you can distribute it, however this would realistically have to be at the inverter not at a distribution board/cu.

If you can get an older type 1 mcb which has a lower instantaneous trip, then you could use a 25A mcb, alternatively if you obtain manufacturer's data for a type B, careful selection would give you a 20A mcb which will operate within time on 100A.

Lastly, it is permissable to use a rcd/rcbo if the fault current is insufficient, however you need to ensure the inverter is correctly earthed and can provide earth fault current.
Thanks for the advice Julie, I'll look into the manufacturer's data for MCBs.
 
Does the inverter have one pole of its output reliably connected to earth? Ie is it providing a TN system or an IT system.
If it does not you should be installing double pole mcbs.
 
Does the inverter have one pole of its output reliably connected to earth? Ie is it providing a TN system or an IT system.
If it does not you should be installing double pole mcbs.
It's a TN system. Neutral and Earth are connected at the inverter output and are also connected to an earthing rod.
 

Reply to MCBs for Inverter-Supplied System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
405
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
640

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock