That is commonly called a vigi module. You will notice when set for 30ma there is a line down indicating to set to no delay so additional rcd protection is provided.
Yes I’ve only seen a couple of these, on another vary similar model it also has the option for ON and TEST which is a good featureThat is commonly called a vigi module. You will notice when set for 30ma there is a line down indicating to set to no delay so additional rcd protection is provided.
Yes all sub circuits and feed from mains all tested fine with IR, now set to 300mA it’s all fine there’s discrimaination now 300mA to 100mA and so on, just didn’t understand the bottom dialSo does that acheive disconnection times satisfactorily now that you have changed it to 3 x the original ma? Is it not the case if it is tripping that some investigation may be due? Maybe IR tests if it is possible?
Yes all sub circuits and feed from mains all tested fine with IR, now set to 300mA it’s all fine there’s discrimaination now 300mA to 100mA and so on, just didn’t understand the bottom dialSo does that acheive disconnection times satisfactorily now that you have changed it to 3 x the original ma? Is it not the case if it is tripping that some investigation may be due? Maybe IR tests if it is possible?
It’s at 1Out of interest,what did you set the delay,to?
???Has anyone set one up before and could tell me? Or know how to
It’s the bottom dial I can’t understand? So it just works on disconnection time but in milliseconds? So say I have no greater than 32A final circuits on TT which is 0.2 seconds then what do I set it?It's a wind up this one. Guaranteed
Ok so it’s TT, in this panel you have Main MCCB/RCD one in picture then 3 X BS88 fuses which feed some electric boxes with 16A sockets with relevant 30mA RCBOsBut you were asking what delay a TT circuit should be set to. Are you saying you know this, but need to convert seconds to milliseconds?
To answer that, there are 1000mS in a Second.