I'm still confused. Do you not know what the regs require, or do you not get the seconds/milliseconds thing?
 
It is a variable earth leakage modual that is used with a mccb eather bolted on or using a shunt trip module

The top part is to set trip current
Bottom is to set a time delay

They are mainly used on sub circuits or large motors ect were the time delay can offer some sort of discrimination

Remember earth leakage is cumulative
Thanks is there a way to understand how to set the time delay?
 
It is a variable earth leakage modual that is used with a mccb eather bolted on or using a shunt trip module

The top part is to set trip current
Bottom is to set a time delay

They are mainly used on sub circuits or large motors ect were the time delay can offer some sort of discrimination

Remember earth leakage is cumulative
Thanks is there a way to understand how to set the time delay?
 
First you need to know what function it is required for. Secondly you need to consider upstream devices and how they are operating then the vigi module can be set to ensure coordination is achieved.
 
First you need to know what function it is required for. Secondly you need to consider upstream devices and how they are operating then the vigi module can be set to ensure coordination is achieved.
It’s TT system so this is the upfront RCD, all there is down stream is 30mA RCBOs at boxes protecting sockets
 
Thanks guys really appreciate your time

So if it was more than 32A TT system I’d set it to 1.0 second for instance?
If you were using it to protect distribution circuits or other circuits greater than 32A, yes you would set it to 1s.
 