HI AGAIN
I HAVE 2 MCCB,s (moulded case circuit breakers ) RATED AT 120A AND 250A THE MAX Zs FOR THE DEVICES ARE 0.12 AND 0.09 MY PROBLEM IS THE Ze IS 0.24 AT THE DB. SO THERE IS MY PROBLEM AMY SUGGESTIONS WILL BE WELCOME
 
Have you tried measuring the Zs? To see what effect any parallel paths may have on your readings.
Also, where did you obtain your max Zs info from?
 
had this problem in a sheltered housing about 1 year ago when working with 3 Rivers housing!!

we changed 3 phase tails to 50mm and it dropped by 0.2ohm...!! end result was to remove the MCCB and insert a 250a tp&N isolator and we then changed all the MCB covering Socket outlets to 30Ma RCBO's big job and very costly but that was the way forward..!
 
Are you sure those Max Zs values are for 5secs disconnection? I commissioned a panel board today of Eaton MEM MCCBs 100A 25kA and the max Zs was 0.4something from manufacturers data
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
north east england

Thread Information

Title
MCCB Zs TO HIGH
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Thread Tags

Tags Tags
mccb

Advert

Thread statistics

Created
albi,
Last reply from
lamb,
Replies
6
Views
5,942

Advert