Hi Folks, Maybe a schoolboy issue, but, the scenario. I have a 3 phase cct for a car ramp. It's fed by a 4mm swa which comes off an MEM board via 3 pole MCB to a 32A TP&N MEM Fused (HRC) isolator. My question is: Does it need to be locally fused or can it just be a switch?
 
Any item of equipment like the one you are describing needs a lockable isolator for maintenance purposes surely.
 
Sorry i was lost in the fusing of it, yes, it would need a local point of isolation, presumably is has one built into of part of the ramp does it not?


I get what your saying but, I would still want to see a local isolator to allow complete isolation so there is no voltage coming into the Ramp control panel. 100% safe then.
 
Surprised it doesn't need an E-stop as well, as it's a large moving part? Not that that's necessarily isolation in this sense, I know.
 
Surprised it doesn't need an E-stop as well, as it's a large moving part? Not that that's necessarily isolation in this sense, I know.

If you introduce e-stops in to a propriety control system then you’d better be sure what you are doing. You could end up on a sticky wicket if anything goes wrong.
 
32amp fused up and downstream is not needed as this will give discrimination issues, If the car ramp has a lockable isolation and requires a tool to access thenyou don't even require an isolator, this applies if its an interlock where access to the electrics cannot be gained without the power been disconnected (except to the interlock supply side which will be marked and finger safe. If the isolator switch does not interlock with the access panel and you can gain access without switching off then all electrics internally will be required to a higher safety standards ....gaurds over terminals, finger safe, warnings etc.... this is usually done where access may be required by the operator to adjust or reset an item.
Regarding the above this applies if a tool is required to access the electrics ..when I say tool I don't mean another word for the operator either I mean a screwdriver or keylock etc.

All this been said its always best to have a separate isolator on the wall etc as this allows other service companies to completely isolate the ramp as some companies now won't service equipment where this is not the set-up.
 
Thanks all. I just couldn't find anything to say either way. I will without doubt make sure there is local isolation as I would have. I just thought it a OTT to stick HRC on a cct protected by MCB.
Cheers again
Steve
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Means of isolation
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
scratchy,
Last reply from
scratchy,
Replies
12
Views
1,769

Advert

Back
Top