32amp fused up and downstream is not needed as this will give discrimination issues, If the car ramp has a lockable isolation and requires a tool to access thenyou don't even require an isolator, this applies if its an interlock where access to the electrics cannot be gained without the power been disconnected (except to the interlock supply side which will be marked and finger safe. If the isolator switch does not interlock with the access panel and you can gain access without switching off then all electrics internally will be required to a higher safety standards ....gaurds over terminals, finger safe, warnings etc.... this is usually done where access may be required by the operator to adjust or reset an item.
Regarding the above this applies if a tool is required to access the electrics ..when I say tool I don't mean another word for the operator either I mean a screwdriver or keylock etc.
All this been said its always best to have a separate isolator on the wall etc as this allows other service companies to completely isolate the ramp as some companies now won't service equipment where this is not the set-up.