I will attempt to explain the requirements for concealing cables in walls:
1. Bury the cable at a depth greater than 50mm.
It is assumed that people will not use screws and nails that are longer than 50mm.
2. Use a cable that has an earthed metallic sheath.
The idea being that if a screw or nail penetrates the cable, the screw or nail will be contact with the earthed sheath, and if also contacts a live conductor, will cause the OCPD to operate.
3/4. Use earthed conduit or trunking.
The idea for these methods are the same as for No. 2.
5. Provide mechanical protection sufficient to prevent penetration by screws or nails.
There is no requirement to earth the mechanical protection as in the case with Nos. 2, 3 & 4, because the screw or nail will not penetrate the cable, will not contact a live conductor and will not be required to cause the OCPD to operate.
6. Run the cable in a prescribed zone and provide additional protection by means of a 30mA RCD.
The idea being that if someone is unaware of prescribed zones, then hopefully the RCD will operate.
Remember, not all conduit is 3mm thick, some is very flimsy indeed, and will not provide the required level of mechanical protection. Such flimsy conduit requires earthing.