This Web article was published last November and highlights the serious issues with hospital wiring that need to be addressed. Amendment 4 will not resolve the major governance issues but will at least give clarification especially on testing the supplementary equipotential bonding in Group 2 locations.

Link to web article
 
It's not easy pinning down some details, but the first thing that strikes me is whether there was a safety case done for the system. That would have considered the risks to be mitigated against - normally being able to kill the power is considered the "safe condition", but as seems to be the case here, losing the machine's medical diagnostic function brought It's own risks.
With my main work hat on, killing the power/stopping things is very much not the default safe state.
 
It's not easy pinning down some details, but the first thing that strikes me is whether there was a safety case done for the system. That would have considered the risks to be mitigated against - normally being able to kill the power is considered the "safe condition", but as seems to be the case here, losing the machine's medical diagnostic function brought It's own risks.
With my main work hat on, killing the power/stopping things is very much not the default safe state.
Hi. Medical x-ray equipment has to have a means of mains power isolation as required by the Ionising Radiation Regulations. A contactor is used so that it is easy to switch off with emergency off mushroom buttons that are shrouded and located in the examination clinical room. FYI a cardiac X-ray unit is rated at 120kVA.
 
Hi. Medical x-ray equipment has to have a means of mains power isolation as required by the Ionising Radiation Regulations. A contactor is used so that it is easy to switch off with emergency off mushroom buttons that are shrouded and located in the examination clinical room. FYI a cardiac X-ray unit is rated at 120kVA.
I guessed that, but what's the SIL for that single contactor and it's control circuits ? Allowing for the limited detail available, it doesn't sound like a properly engineered, and properly maintained, system.
 
I guessed that, but what's the SIL for that single contactor and it's control circuits ? Allowing for the limited detail available, it doesn't sound like a properly engineered, and properly maintained, system.
Currently there is a gap - which is why I wrote the article. I understand that at least industry will be responding in the form of a useful guidance note soon. Drafting it also helped to identify there is actually a BS standard on the indicator lamps required for cardiac labs as there is a specific standard.
 