Hi guys & gals,
I gave in and bought the new Megger MFT-X1. Got my hands on it Friday night, had a little play with it, used it at work on Monday and wrapped it back up on Monday evening, ready to send back...
I've been using my megger 1720 for about 7 or 8 years for domestic and commercial testing and lots of fault finding and I wanted to start testing EV chargers, hence I bought this new beauty. But soon I realised that's all it is, a beauty.
Now I was looking online for non sponsored reviews to see if anyone is experiencing the same level of frustration as me but I can't seem to find any. So I started writing a list of pros and cons, the latter a lot longer unfortunately.
Here comes the list... Please tell me if I'm wrong in any way and try to convince me to keep it, although I think it might be waste of breath.
Pros:
- It can test EV chargers but so can the 1741+
- I'm really "flipping" struggling here.
Cons:
- No proper auto start for live tests like in the 17 series. You need to "prime" the test by pushing the test button before touching live terminals for Zs or RCD. Can't just plug it in and wait for it to start.
- Insulation resistance test takes 5 seconds of loading before it shows you ANY reading.
- Newly designed croc clips that come with it are rubbish. Rounded in the middle so wires slip out.
- No normal probes come with it. Only some oversized long ones.
- Doesn't come with padding for the neck strap and the neck strap has 2 tiny buckles on it for no apparent reason. They're just there to snap and drop your tester as a result.
- The current test is barely used by anyone in domestic or commercial. Why do I have to turn the dial past it every single time when I want to go to low Ohms or MOhms tests... If we want to measure amps, we'd just use our simple clamp meter/voltage indicator with clamp on it.
- It's heavy.
- It says you can get a battery carrier for AA batteries but that's not available (yet) . So if your rechargeable battery dies, you'd have to wait 30min to charge it. That's about a quarter of the time it takes me to do a full EICR. (Apparently 30min charge gives half a day of usage).
yes, but when rules change again you can update it without buying a new one
I'm not impressed of the new tester looking on a download, nearly 2 grand, where some manufacturers like metrel and kewteck nearly the same price
Shows you how to test and a indecator pass or fail.
Got mine a few weeks ago. I find the operation easy enough once you get over the fact it doesn’t auto live test once it sees the voltage.
had a problem with the battery not charging fully, my wholesaler swapped it straight out for a new tester at the instruction of Megger.
we have several older Megger units and this one isn’t really that different. I liked the idea of firmware upgrade without having to replace the teste.
not sure where people are getting £2k price from as mine was significantly less than that, perhaps a little negotiable with the wholesaler 😉
Are you a megger rep?
@Biggron maybe you can answer a couple of things someone told me last time I was at City.
I asked him how he was getting on with it, his summary was "they haven't got it right yet". I asked for more info:
Firstly he reckoned that all the loop tests were low current and he couldn't make it do a high current. I seriously doubted this - can you confirm he was missing something? It looked as though one of the top function keys changed it but I didn't try this myself when I played with one.
Secondly (more believably) he reckoned the ability to store results and beam them to software relies on doing the tests in the order they want. (This is a bug bear of mine as I want to do IR testing last when the containment is back together, not work through one circuit at a time.)
Oh I don’t think it’s perfect but what tester is? A lot depends on what you’re comfortable with.
Yes you can change the individual settings of each test function, at first I thought it was by just the top function buttons but by accident also found out the right hand dial can do so as well.
As for the storing and beaming of results (only to icertify I understand) I can’t comment as that’s not something I’m interested in using as we use the nic portal. I did listen to a comment from a fellow spark who hadn’t got it to work smoothly yet.
Reactions: timhoward
I seriously considered the X1, my main interest being that it should be able to connect to a laptop and auto-fill the results. This would remove any chance of an error due to my dyslexia. Currently I photograph my 1730 for certain readings as a double check against my notebook entries.
However, I'm not convinced more time would be saved than my (admittedly inefficient) notes+photos method; Bluetooth just ain't that reliable and I certainly do not want to be locked to one piece of software for anything. Comments about the croc's etc are interesting.
Did megger make a tester has a toy, winder it up and off you go, me I still use me megger 1720 thinking should I by a x1
Thinking not when you have got other manufacturers doing better.
Hi guys & gals,
Pros:
Cons:
- It's heavy.
View attachment 111093View attachment 111094View attachment 111095View attachment 111096
Spot on. I have exactly the same problems with X1 unfortunately
Reactions: wrpizza and Montyg
Hi guys & gals,
Pros:
Cons:
- It's heavy.
Hi guys & gals,
Pros:
Cons:
- It's heavy.
Patrick
Megger have just sent out 4 updates for this model which covers the issues you have picked upon.
There are 2 sets of clips the grab clips are great,
Regarding the strap yes that is poor
Also the Bluetooth doesn’t even work yet.
Reactions: Montyg
Gave up on Megger when a 1700 series died on me whilst testing a campsite - failure of IP rating. And then when I ordered another 1700 series it arrived with the top and bottom not being joined together!
Cant say the X1 fills me with any confidence.
I just sold a 1720 upgraded to a 1741 plus, opened the box, and found one of the red buttons was crooked and sent megger a nice letter, I had a rep pop
Over to sort it out,
Had to pop over to a job where a friend was testing an installation with his MFT X1.
He was testing a smoke circuit with 5 detectors installed.
He found that when trying to carry out a RCD x 1 @ 30mA and 3 or more smokes heads were attached to the bases, the tester would fail >300ms.
If 3 or less heads were fitted, then test would come back around 29ms.
He spent hours testing each leg of the circuit for faults (all fine), changing the combination of smokes, changing the test settings rcd type and even replacing all the smokes but still the same outcome.
I told him to swap the rcbo over for one he’d tested to rule out a fault rcbo.… but the same thing happened.
I told him to try a small load on the circuit by fitting a pendent / led lamp on the last smoke base but remove all the heads… The rcd test passed this time.
Thats when i headed over and tried my 1741+ to test the circuit. Set to rcd auto / 30ma and low a behold with all the heads attached I got a complete set of reading all within the required times.
It would appear some of the sensitive electronics in the heads has an effect on the X1 rcd testing. He’s made the call to megger.
It’s not the only issue he’s had with it either. It’s been sent back twice before.
To be honest, like the op said, it’s a vanity unit. If you have a functioning MFT already it really is a waste of money… And now a worry for my mate who is questioning his passed readings.
I have said before most manufacturers
are way a had of megger, it's OK to make a new tester, look at others first and improve theirs.
A during conversation I had with a technical guy at Metrel a number of years ago he said that the rotary test selectors on MFT's were a cause of a number of random test errors in most manufacturers kit which is why they moved away from them
I think the problem with test kit is that many looking to buy new and to some extent used kit tend to go with the more well known brand names of Fluke and Megger without comparing the specs and also those of the lesser known manufacturers
For me the new Megger MFT doesn't look like a rugged piece of kit and gives the impression of more of a glossy cover with little substance inside
I’ve tried one for two weeks and I’m keeping it.
The main things that convinced me:
1 user updatable firmware, so putting some trust in Megger here, quirks will get resolved in due course
2 the data transmission to CertSuite is brilliant, saves me time on jobs, and saves me time in evenings doing less admin
Main gripes:
  • IR test are irritatingly slow, I’d never use it for fault finding
  • delay when changing modes while is shows you Disney graphics
  • auto test start isn’t - you have to press test to arm it.
  • for all that money they could give you a neck strap for the tester! (To be fair you do get a lot of good kit with it like long leads and earth stakes for fall of potential rod tests.)
I’ve not yet have any issues with actual testing with it.
Certsuite or Vespula as it was is a good cert package and reasonably priced, I've been using it for about 4 years now
Hi guys & gals,
Pros:
Cons:
- It's heavy.
How I wish I’d read this 6 weeks ago before I bought the thing. All you say is true and my strap did give way sending the tester plummeting to the floor. The fall was only slowed and softened with the test lead (now showing signs of damage) and my foot. Megger don’t really seem that interested said they would send me the new improved strap which still hasn’t arrived not offering to check over the machine after its fall or even send a new test lead despite me send photos and keep closing the complaint ticket despite them not resolving anything. If I hadn’t already had it six weeks I’d return it to CEF for a refund. Will be getting my 17 year old 1553 repaired and using that instead I think.
Appalling customer service so far.
That's shockingly painful to see your brand new tester going down like that. Sorry mate.
I've never used the neckstrap tbh. I've had my fannypack megger bag for years and love it. (Megger 1006-408).
That was the primary reason given to me by the sales team. It does feel as if every other factor got forgotten. They tacitly admitted, the colour screen draws more power but other manufacturers had gone colour. I've been Megger since college but might have to be Kewtech next purchase
How's everyone finding the x1 with the latest firmware updates?
I'm after a new mft unsure whether to go with the x1 or try find a good used 1741+
Unless you specifically want to send results to CertSuite I wouldn’t bother. And even that I’m not that impressed with. Some situations it saves a little time but more often than not I find myself not using it.
In fact stay don’t get a Megger.
The X1 was been back for repair to manufacture twice in the first 6 months from new. Had hardly any use and always been looked after. In fact I have so little confidence in it that I take my old Fluke with me as well so when the megger fails again I can revert back to that!
The 1741 I had again went back to Megger within months with a fault. That now has fluctuating results. It’s the ports for the test lead. Common fault with them.
I certainly won’t buy another from them. The old fluke I have is bomb proof and more accurate consistency!
I purchased a x1 last week but not had chance to give it a good try out yet although on first glance it does seem abit to complicated. What don't you like about it?
I've got a 1720 that's gone in for repair but I to was getting flucating results with the megger leads. I've changed the leads to a set of kewtech and readings have been spot on since. The only reason I was looking for a new tester was because of the rcd uplift that the 1720 suffers from
Harlow
Megger MFT-X1, definitely a step backwards.
Electrical Tools and Products
wrpizza,
slacky1230,