It's not unusual to get a higher reading on a low current loop test than on a normal loop test and therfore the calculated fault current will be lower.

This has been referred to as 'RCD uplift' by some people as it can be the result of impedance through an RCD though the same problem can occur with low current tests when there is no RCD in the circuit.

This is one reason why a high current loop test should always be used whenever possible.
 
It's not unusual to get a higher reading on a low current loop test than on a normal loop test and therfore the calculated fault current will be lower.

This has been referred to as 'RCD uplift' by some people as it can be the result of impedance through an RCD though the same problem can occur with low current tests when there is no RCD in the circuit.

This is one reason why a high current loop test should always be used whenever possible.
thought maybe new megger X1 may need a software update , purchased today but calibration sheet was april 23 . done same test on MFT 1711 and both were similiar readings, however rcbo tripping on no trip low on 1711 crabtree starbreaker i always seem to get them tripping, i reverse earth in phase and phase in earth socket on megger and test runs ok , no problems on new X1 just the unusually high PEFC
 
IMHO this is the best way to get accurate two-wire (high current) loop test data when the circuit is protected by an RCBO or RCD.


And here's the quick graphic I made for my assistant to explain why it works:

1695891644441.png


I regularly use this to get a loop test at a light switch using a 1553 (which has no 2 wire no-trip test)
You just have to remember to take the link out!
 
Last edited:

Reply to Megger X1 PEFC readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I purchased my Megger X1 in July last year so only 7 months old, having been a Megger fan for 20 Years... I've now had the opportunity to get...
Replies
1
Views
580
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
1
Views
235
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
646
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi gents and ladies, I’ve just bought a Kewtech KT63, the instructions aren’t very clear on lead setup. When doing a Ze is this a 3 lead test on...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock