-Matt

Regular EF Member
Customer has this 110KW (converted to 55KW) motor powered via a generator.

They had a problem with the generator cutting out on startup showing overload fault.

Having investigated this issue, along with the motor overload having been bypassed!! (will be rectifying this!)

when I took the cover off the motor I noticed the nylock nut had melted its plastic with signs of overheating.

whilst removing the link bar to test the coils, I found the whole terminal post had melted out of the insulating section. and pretty corroded terminals.

My assessment is a poor connection on the terminal posts .

The coils seem ok.

Im trying to get a motor expert to come out and give his opinion and repair option. however having trouble getting someone out quickly, and customer needs this running ASAP.

Can anyone think of a temporary or permanent, safe fix?
I guess it really needs new terminal block and posts?

What do you guys think?

IMG_2239.JPG


A0D60D25-C534-4971-9122-19DD222C1AAE.JPG
 

telectrix

Scouser and Proud of It
Respected Member
gorilla snot glue. :p:p:p
 

Wilko

Electrician's Arms
Hmm - someone has troubled themselves to bypass the thermal overload and now terminal plate has melted. Is the motor running overloaded or am I reading too much into this?
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
You may expect one post to fail for some reason but to me they are all showing signs of overheating. Get a specialist to look at it and don't attempt an ad hoc repair.
 

snowhead

Respected Member
Ulimately a new block.
They're fairly standard, has the customer got an old / spare motor around?

But, you'll need a new crimp on the ends coming from the windings (or clean the existing up).

As W10 above, they all look to have damage, so clean up all the ring crimps from the windings and nuts /screws.
And the supply cables.

Then new ring crimp onto the supply cable, use a new /clean screw / nuts and washers to the damaged one.
Heat shrink over the joint if you've got any big enough (put on firts of course) tie wrap the joint away from the block so it doesn't bounce around.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
I would want to know why they have ended up like that, yes a new block can be fitted but long term do you end up in the same situation or worse.
 

-Matt

Regular EF Member
Hmm - someone has troubled themselves to bypass the thermal overload and now terminal plate has melted. Is the motor running overloaded or am I reading too much into this?
I suspect it was a temporary bodge that was never rectified, its been like that any least a year.

I actually measured the running currents of this motor a few weeks ago (with aim of getting onto grid supply) and it varied from around 50-100A, which FLC of 97A for a 55KW motor seemed ok.


You may expect one post to fail for some reason but to me they are all showing signs of overheating. Get a specialist to look at it and don't attempt an ad hoc repair.
Hopefully a specialist will get out tomorrow.

How has it been converted to 55kw.
That is a question I asked, but they don't know was the answer...
 

ipf

Forum Mentor
If they were solid connections, I find it difficult to understand why a terminal would burn out like that before a winding going down.
Looks like a complete rewind and terminal block, who knows the internal damage done. How do the windings read?
 

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.