looking at a job where the Meter is in the Detached Garage and CU in the house, approx 15m run. Best ideas. Run SWA from isolator in garage to CU? and separate Dist. Board for garage supply from same isolator?
Cheers
G
 
Is it an existing or new build?

Will need seperate switched fuse located in garage to run the swa from, if locating the cu in house.
 
Is it an existing or new build?

its a existing build, needing a full rewire, yes will get EON to fit isolator and was then going to fit secondary isolator to then split to garage dist board and house CU. mainly to terminate swa cable.
80 or 100 amp rating depending on EON main fuse. prob 100amp though, which means large csa swa cable to house, agree??
 